  • #11734

    jonyskiw
    Member

    I have experienced the same problem after installing a new battery. It worked fine for about 4 days then after performing its daily automatic battery check it now beeps every 50 seconds, except the beep sound comes from the ceiling sensor/speaker not the keypad. I have powered down the system twice for about 1 hour but the beep starts again and occurs every 50 seconds.Why is this occurring?

    #53010

    Old EW Tech
    Keymaster

    Welcome to the forum.

    Let us know the make/model of the device on the ceiling and we can move on from there.

    #53097

    jonyskiw
    Member

    The Security System is a Moose Z1100e Security System Control with 8 zones. There are 3 keypads (all on the main level) and 3 ceiling smoke detectors (one on the main floor and 2 in the finished basement). Only the smoke detector on the main floor beeps every 50 seconds. Here are the markings:
    Dicon Systems Ltd (Toronto, Canada)    330 SR 12/24 ionization type
    12 or 24v AC/DC  145mA and a sticker with NP22
    There are 3 LED lights lit (solid green, not flashing) on the keypads:
    Power, Interior On, and Delay.

    #53099

    Old EW Tech
    Keymaster

    Try resetting the detector by pressing 7 + code (Smoke Reset and Battery Load Test).

    Let us know the results.

    #53115

    jonyskiw
    Member

    The reset has stopped the beep… had to do it twice, but it worked and has been silent ever since. Have to see what it does when the automatic battery check is performed tomorrow.
    Thank you for the help

    #53117

    Old EW Tech
    Keymaster

    Good, glad that you got it.  :)

    #53817

    jonyskiw
    Member

    It seems my problem is back.
    Ever since the daily battery check occurred earlier today a beeping sound  now comes from the ceiling sensor/speaker (smoke detector) every 50 seconds. I have tried several times to reset the 'smoke detector' by pressing 7 + code as per your previous instructions (on Jan. 10/11) but to no avail.
    The Security System is a Moose Z1100e Security System Control with 8 zones. There are 3 keypads (all on the main level) and 3 ceiling smoke detectors (one on the main floor and 2 in the finished basement). Only the smoke detector on the main floor beeps every 50 seconds. Here are the markings:
    Dicon Systems Ltd (Toronto, Canada)    330 SR 12/24 ionization type
    12 or 24v AC/DC  145mA and a sticker with NP22
    There are 3 LED lights lit (solid green, not flashing) on the keypads:
    Power, Interior On, and Delay.
    Any thought as to why this is occuring again.

    #53843

    Old EW Tech
    Keymaster

    That model smoke detector was discontinued some time ago.

    Given that the detectors are probably the same vintage as the system and the fact that the detectors have a recommended useful life of 10 years, I'd recommend that you replace all three.

    #54035

    jonyskiw
    Member

    Where would I be able to acquire these replacement units… I am in Western Canada?

    #54037

    Old EW Tech
    Keymaster

    We can't tell you where you might be able to purchase locally; however, we sent you the forum's list of recommended online resellers of alarms and alarm related equipment.

    The ESL 449CST or System Sensor 4WTABA would be my suggestions for replacements.