Home Forums Ademco Technical Questions Contact ID Report Codes – Alarm and Trouble

This topic contains 1 reply, has 2 voices, and was last updated by  vector18 3 years, 8 months ago.

Viewing 2 posts - 1 through 2 (of 2 total)
  • Author
    Posts
  • #11223

    ryano2121
    Member

    I am programming a zone type 90 configurable zone on a SafeWatch 3000EN through ADT.  How can I find out what my Contact ID Report Codes for alarms and troubles?

    #50820

    vector18
    Member

    In *56 each zone tells you the report code. If your using contact ID, you can put 10 as report code for every zone. The purpose for contact ID
    is the panel actually disregards the actual report code that you have and tells the central stations receiver for example, if Zone 1 is a exit/entry zone, it tells central station that zone 1, type entry exit, alarm. It actually
    does not transmit the report code that you have programmed. Only if your using 4+2 or 3+1 report format instead of contact ID will the panel
    actually use the actual reporting code. Hope this helps you out Ryan.