  • #19297

    dalepres
    Participant

    I have two questions; I hope it's OK in one thread.I have a door switch on the front door I am connecting to my RFK5500

    #80064

    blakem
    Participant

    Hi dalepres I am a fellow EE myself, For the first question there is no zone type as you describe, but what I would do is program the front door to an entry delay zone.

    #80068

    brandonlive
    Participant

    I agree with Blakem, but the one thing I wonder is whether your outdoor PIR will only be tripped once per visitor.

    #80120

    dalepres
    Participant

    Thanks for the ideas, both of you.

    #80996

    dalepres
    Participant

    Ok, I got the PIR and ELK-120 tested, configured, and, I thought, set up but I can't get the PGM output to trigger the ELK-120.On the Elk, on the workbench, I can jumper from the VS- to ground and it plays the message I want it to play; perfect.I took it to the equipment closet and hooked it to the PC1832 but I can't get a peep out of the Elk.I started with PGM1 and the following settings:*8 [install code][001] 01 00 26# (zone 3 is the outdoor PIR).[009]29#[501] (only option 3 is set and that was the default)[551] (cleared all zones except 3)When I walk test the PIR, the LEDs come on but the keypad chime doesn't work with zone type 26.

    #81001

    blakem
    Participant

    It looks like you assigned PGM1 to partition 3 when you modified section [551].

    #81082

    dalepres
    Participant

    Thanks for the reply.From ste statement quoted below, I understood that 551 to 564 program the PGM output partition associations for most PGM types but for zone followers they are used to set the zone.

    #81125

    blakem
    Participant


    Zone Follower PGM types 29 and 35-41 are used to assign specific zones to the PGM.

    You are right, I must have gotten mixed up but yes for that PGM type the parition assignment acts as the bitmask for the zone follower.

    I verified option 3 is on for section [103].

    #81131

    dalepres
    Participant

    Thanks.

    #81133

    blakem
    Participant

    You could do a pull up resistor in case it is just floating since it is an open collector, but i ment use a current limiting resistor and an led to test the output.

    #81142

    dalepres
    Participant

    Gotcha.

    #81237

    dalepres
    Participant

    I got it working to drive the Elk-120 from the DSC PGM2 for now using a relay driven by PGM2 to switch +12v to the Elk to play the message I wanted.The zone follower works right but the panel won't beep on the zone follower set to 26 zone type.

    #81238

    dalepres
    Participant

    I forgot to add some details of how I fixed it.

    #81244

    blakem
    Participant

    That is great you got the two systems integrated.

    #81268

    dalepres
    Participant

    That is great you got the two systems integrated.

Viewing 15 posts - 1 through 15 (of 15 total)